The light would only be associated with the tenant that is suppling it.210.25 Common Area Branch Circuits.
Branch circuits in dwelling units shall supply only loads within that dwelling unit or loads associated only with that dwelling unit. Branch circuits required for the purpose of lighting, central alarm, signal, communications, or other needs for public or common areas of a two-family or multifamily dwelling shall not be supplied from equipment that supplies an individual dwelling unit.
this statement talks about the dwelling. Not about the land around it.needs for public or common areas of a two-family or multifamily dwelling
210.25. Add an exception as follows:
Exception: Branch circuits supplying lighting outlets in common areas on the same floor as a dwelling unit in a new or existing two-family or an existing three-family building shall be permitted to be supplied from equipment that supplies one or more of those dwelling units.
I agree, I see that in the NEC now. I was just used to MEC rules which allow me to do so.Originally posted by jap2525:
210.25 does not allow common area lighting to be fed from an individual dwelling unit.it must be fed from a house load panelboard.
The structure is the pole. The structure is permitted to be supplied by ONE service only.Article 100
Service. The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.
Structure. That which is built or constructed.
230.2 Number of Services.
A building or other structure served shall be supplied by only one service unless permitted in 230.2(A) through (D). For the purpose of 230.40, Exception No. 2 only, underground sets of conductors, 1/0 AWG and larger, running to the same location and connected together at their supply end but not connected together at their load end shall be considered to be supplying one service.
Even if this was on the same property AND under single management, the structure still is not allowed to be supplied by more than ONE feeder or branch circuit.ARTICLE 225 Outside Branch Circuits and Feeders
225.1 Scope.
This article covers requirements for outside branch circuits and feeders run on or between buildings, structures, or poles on the premises; and electric equipment and wiring for the supply of utilization equipment that is located on or attached to the outside of buildings, structures, or poles.
II. More Than One Building or Other Structure
225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
It?s hard without a picture. Normal current flow is from the panel, via a breaker, via the hot leg, to the light, via the cold leg, back to the source. There is also an EGC that connects to the case (i.e., light pole) to the panel, via the bonding jumper to the neutral, and thus to the source. This situation has two such circuits, and has the two EGCs connected to the same point at the light pole. Please note that the two breaker panels need not be from the same utility source, and certainly need not be from the same phase.Originally posted by iwire: Charlie B I do not understand how we are going to raise the voltage through a high impedance fault. . . . can you explain it in a different way?
The "service" stops where the premises wiring system starts. Article 230 stops where the premises wiring starts.The definition of "service" states that a service delivers energy to the premises wiring system.
Premises Wiring (System). That interior and exterior wiring, including power, lighting, control, and signal circuit wiring together with all their associated hardware, fittings, and wiring devices, both permanently and temporarily installed, that extends from the service point or source of power, such as a battery, a solar photovoltaic system, or a generator, transformer, or converter windings, to the outlet(s). Such wiring does not include wiring internal to appliances, luminaires (fixtures), motors, controllers, motor control centers, and similar equipment.
The rules in 225 and 230 are parallel, but Article 230 applies to the service and Article 225 to the premises wiring system. If both sets of fixtures are of the same voltage, then you can cite a violation of 225.30, however if the contractor or engineer is sharp, he or she can take advantage of 225.30(D) and make an installation is in compliance with the NEC rules.Service Point. The point of connection between the facilities of the serving utility and the premises wiring.
None of the rules permit more than one source of power to feed one piece of equipment that is not designed or listed to operate or be installed in that manner.
When it comes to a question like this, it is not a matter or what you or I want, it is only a matter of what the code rule says.If there were a premise that actually had more than one service, and you were trouble shooting a piece of equipment, would you not want to know "which service" was supplying power to the equipment as opposed to just which branch circuit or feeder?
Don