2008-Article 300.3(C)(2)(c)
Do you interpret the word enclosure to include raceway as mentioned in 300.3(C)(2) at beginning.
This pertains to motor space heater leads being routed in same cable tray as the power feeders.The power conductors are not energized when the space heater leads are.
I'm reading from the 2008 Code. It seems in the past this was allowed and it may have been earlier than 2005. I guess it could have been an owner allowed thing too.
Just curious,as I have this situation coming up but have a control(600) tray available, so no big thing if needed.
dick
Do you interpret the word enclosure to include raceway as mentioned in 300.3(C)(2) at beginning.
This pertains to motor space heater leads being routed in same cable tray as the power feeders.The power conductors are not energized when the space heater leads are.
I'm reading from the 2008 Code. It seems in the past this was allowed and it may have been earlier than 2005. I guess it could have been an owner allowed thing too.
Just curious,as I have this situation coming up but have a control(600) tray available, so no big thing if needed.
dick