The POCO requires them here; they call it a Load Letter.Are load calculations required for residences? Certainly not around my parts, but I am wondering if we're just not doing things right.
The power company probably put a transformer in that was under sized for the actual calculated load anyway.When my daughter had a 1900 sqft home built in 2013, the quote from the GC included a 320 amp service. Home has gas furnace, range and hot water. I questioned him on it and his reply was that all his homes get a 320.
So I did a load calc and she saved some money with a 200. The guy had never heard of a “load calc”. He just tells his EC to put in a 320 and that’s what happens. IDK if the utility cares or not?? I don’t recall the actual calculation result, but I suspect a 100 would have been close to covering it.
Bottom line - it’s probably a good idea to do one even if not required. And based on my experience, it’s never required here.
And they probably mostly concerned with things like electric heat, air conditioning, water heaters, and not so much about exactly how many square feet and the NEC general lighting load associated with those square feet.The POCO requires them here; they call it a Load Letter.
I never shown an inspector a load calculation in my life. That said if I had a really obvious undersized service/feeder the topic likely to come up.I agree it to be a good practice. But I am wondering if it's ever required by L&I? Maybe inspectors are allowed to make judgment calls if they see red flags?
Good save. That is kind of random though... a 320A service?? and for a 1900sqft house?? I guess I'll need to run down to Homedepot and pick some of them new SquareD 320A main service panels.When my daughter had a 1900 sqft home built in 2013, the quote from the GC included a 320 amp service. Home has gas furnace, range and hot water. I questioned him on it and his reply was that all his homes get a 320.
Well it is common and even required in some places to install 200 amp minimum even though the demand may never be close. Even on limited load single circuit applications you may find some POCO's demand 200 amp supply to the metering equipment, where you otherwise could satisify NEC with 30 or 60 amp service conductors.When my daughter had a 1900 sqft home built in 2013, the quote from the GC included a 320 amp service. Home has gas furnace, range and hot water. I questioned him on it and his reply was that all his homes get a 320.
Oh no... I am well aware of how the meters work... but for the GC to say "Hey... Mr. Electrician... throw in a 320A service!"... 320 isn't a round number to me hahaha. 150, 200, 300, 400... those are numbers I like to work with.Not random at all, just what a 400 amp residential meter base is rated for! Here on Dominion we call them 400 amp services, but that Durham meter base they hand you is rated for 320 amps.Still wire two 200 amp service panels to the meter base.
Up in SMECO territory (Southern Maryland Co-Op), a co-worker wanted a "400 amp service", and SMECO said, nope, 350 amp is maximum we supply. Use one 200 amp panel and a 150 amp panel! That was back about 2006.
ALL new residences on Dominion and the surrounding Co-Ops require a Load Letter. So while the inspector never sees it, you do not get power without one!
320A is the actual rating of the largest in-line socket you can get. And it is suitable for a 400A service if the main is not 100% rated. The socket is UL listed for 25% temporary overload capacity.Good save. That is kind of random though... a 320A service?? and for a 1900sqft house?? I guess I'll need to run down to Homedepot and pick some of them new SquareD 320A main service panels.
I always include my service load calculations on whatever residential permit drawings I am sealing. It proves to the owner that the service is not over-designed and the plan reviewer or inspector that it is not under-designed.
You can serve a pretty big house at 100A, even with air conditioning, if all the appliances are gas. But 200A is the new minimum single-family service size in the Real Estate Sales world, even if everything is gas that can be. It's a "mine is bigger than yours" status thing.
320 amps is stupidly oversized. I did load a calculation on a 2040 sq ft house recently and it was 108 mostly because it had two heating systems with AC (duct issues).When my daughter had a 1900 sqft home built in 2013, the quote from the GC included a 320 amp service. Home has gas furnace, range and hot water. I questioned him on it and his reply was that all his homes get a 320.
You live in the land of high electric rates.Strictly speaking, the NEC requires that all services and feeders be rated for the calculated load. So any AHJ could ask you for one, and how do you know it's compliant if you haven't done it? There's no exception for residential vs. commercial (although the optional calc methods for resi are more lenient).
Reality of enforcement is as many have described already in this thread. My two cents... Many if not most residential installations are way oversized per the NEC because a little extra in material is less than the opportunity cost of spending your time doing load calcs, let alone coming back because someone tripped their main breaker. I've done quite a few load calcs to justify downsizing main breakers for solar installs to comply with article 705. I've yet to encounter a single family home that exceeded 200A, and many are less than 100A.