Obvious undersized service is easy to notice once you've done many calculations is the only time I have asked- I only know of 1 code section that may have reason for call out by AHJ & it is kind of far fetched - I think it could apply for services in residential over 400 amps since:
IRC 2015 E3401.3 Not covered. Chapters 34 through 43 do not cover the following:
1. Installations, including associated lighting, under the exclusive control of communications utilities and electric utilities.
2. Services over 400 amperes.
NEC 2017 - 215.5 Diagrams of Feeders. If required by the authority having jurisdiction, a diagram showing feeder details shall be provided prior to the installation of the feeders. Such a diagram shall show the area in square feet of the building or other structure supplied by each feeder, the total calculated load before applying demand factors, the demand factors used, the calculated load after applying demand factors, and the size and type of conductors to be used.
IRC 2015 E3401.3 Not covered. Chapters 34 through 43 do not cover the following:
1. Installations, including associated lighting, under the exclusive control of communications utilities and electric utilities.
2. Services over 400 amperes.
NEC 2017 - 215.5 Diagrams of Feeders. If required by the authority having jurisdiction, a diagram showing feeder details shall be provided prior to the installation of the feeders. Such a diagram shall show the area in square feet of the building or other structure supplied by each feeder, the total calculated load before applying demand factors, the demand factors used, the calculated load after applying demand factors, and the size and type of conductors to be used.