The only place I know of that it's required is in the service disconnect. {230.75}
For most applications there is no requirement to break the neutral with the disconnect switch. If you do break it, it must be simultaneously or after the ungrounded conductors are opened, as well as simultaneous or first make when closing the switch.WHAT IS THE CRITERIA FOR BREAKING NEUTRAL OF DISCONNECT SWITCH?CODE REFERENCES PLEASE?
You are not required to break the neutral with the disconnect. If you do, it must open simultaneously with the ungrounded conductors.what about disconnect switch serving AHU/Ac unit unit having it's builtin controller inside?
You are not required to break the neutral with the disconnect. If you do, it must open simultaneously with the ungrounded conductors.
Most units like you are describing will not have a neutral, in North America anyway.
400/230 volt Y system?i have neutral at field wiring because there is an auxiliary transformer 230V
Even though the system is not specifically mentioned the NFPA is an "International Codes and Standards Organization" which is the reason some things are mentioned in the NEC that are not used in most areas.400/230 volt Y system?
If so does NEC apply? NEC wouldn't require breaking the neutral but such a system is not normally in areas where NEC does apply, I think.
NFPA wants to be international, they are not everywhere though.Even though the system is not specifically mentioned the NFPA is an "International Codes and Standards Organization" which is the reason some things are mentioned in the NEC that are not used in most areas.
For example, I don't think flammable anesthetics are used in US hospitals however they are in some other countries which is the reason they are still mentioned in article 517.
Roger
Look at the cover of your code book. That doesn't mean it's adopted by every country but it is used as a guide by many.NFPA wants to be international, they are not everywhere though.
For most applications there is no requirement to break the neutral with the disconnect switch. If you do break it, it must be simultaneously or after the ungrounded conductors are opened, as well as simultaneous or first make when closing the switch.
Not sure if it is "the" reason, but if the POCO or feeder neutral is compromised, then the neutral wire could end up at a potential above ground. By opening the neutral too you can be more assured that no electrical energy is entering the dispenser.what is the technical explanation behind breaking neutral feeding dispensers?
You may use a 4 pole disconnect switch in addition to any surge protector to switch off any vulnerable equipment to be protected from severe surges during a thunderstorm.WHAT IS THE CRITERIA FOR BREAKING NEUTRAL OF DISCONNECT SWITCH?
One more advantage of using a 4 pole disconnect switch is a surge would not pass over its disconnected neutral contacts to endanger maintenance personnel servicing an equipment.
First, what is the difference between a switch and a disconnect switch?Explain this surge.