If it is a ground, or not a feeder or branch circuit?
Then are these the categories:
1. Feeders (current carrying)
2. Branch Circuits (current carrying)
3. Control Circuits (not current carrying?)
4. Ground (not current carrying)
To save space and materials if I have a 3/4" EMT with 8 current carrying branch (circuit) conducts and want to add 3 more control wires can I? I'm not exceeding my conductor current rating after derating and I'm not exceeding my conduit fill.