I don't know what you may be getting at with high power factors. AC induction motors naturally have low power factor for one thing. Maybe you meant demand factor? Motor starting doesn't last long enough to be a problem with typical demand factor charges other than maybe for some cases with a high inertia load that takes a very long time to accelerate.Wouldn't a soft start be a good idea where high power factors are a problem.
I can understand not using them on part winding starts. I would think a PW would have problems.
There was a young hvac tech that burned out a compressor that was part winding start because he held in a contactor.
Part winding starting is nothing more than one possible equivalent of reduced voltage starting. Not exactly reduced voltage but you lessen the surge current by only energizing part of the windings for a brief time, once the surge current has dropped off and hopefully you have some rotation in the motor, energizing the second part of the winding won't have such a high surge effect either. Placing soft starter in line with PW controls is rather pointless when the soft starter alone would provide overall better control. The young tech likely held in part of the winding which accelerated the motor, maybe or maybe not to full speed depending on loading conditions and the second winding never was energized leaving the motor trying to drive the entire load on only part of the windings. The delay between part and full windings on normal startup is like only a couple seconds at the most but often much less than that, usually just a bang bang between the steps.