When using the General Method to size the service of a single family dwelling, it is a requirement to increase the largest motor by 25 percent. The question is, which is the largest motor? For example:
A 1 hp motor at 230 volts has a FLC of 8.0 amps and a VA of 1840
A 1/2 hp motor at 115 volts has a FLC of 9.8 amps and a VA of 1127
Section 430.17 requires the FLC to be used in determining the largest or smallest rated motor, but I don't think it applies to Part III of Article 220.
It is a common practice to do service calculations using VA. It seems to me that the motor with largest VA should be inserted into the calculation.
Any input would be appreciated