How would you feel if that section of T-bar was carefully and reliably bonded to the EGC?
-Jon
I have never seen a T-Bar ceiling that was bonded in the way I am looking at tripping a breaker under fault. It lays in a grid system and held up by wires for the ceiling. It was never designed to do what we are asking it to do. I have never seen a T-bar that would accept a 10-32 ground screw by design.
This system as shown is closer to driving a 10' rod in the ground for service and hoping that would trip a breaker under fault.
I do not have the expertise to do what you are asking for. Plus, if I did do that, would the inspector like my DIY bonding? This is being done to clear a fault. What would the inspector deem, "reliable"?
Now, if you are asking me if the T-bar was bonded based on a UL test that it would trip a breaker under fault, then yes, I would have no issues with that.
The easiest way to fix this, (other than the wire fill issue might be a problem per code), is to make that one Tee plastic. Problem solved. If it's in the main runner, then off to the ceiling manufacturer to solve that problem. These guys will sell anything at the right price. It's a great product. It would make sense to pursue.
Of course, as soon as the code guys look at this and see its now part of this tee system, or imply that is, who knows where that will go. Thinking about this, I've already ditched the Caddy - 512 brackets that cost a bundle for this installation! Contractor is already looking on how to save a buck!