I’m installing utility pad-mount transformer underground.
Relevant details:
•Spec calls for (2) ¾” x 10’ copper-clad ground rods.
If I drive the rod from the bottom of the 4’ excavation:
So it seems the only way to both:
Is to backfill/bring the area up to near grade and then drive the 10’ rod from that elevation.
Is that the correct interpretation of “driven to a minimum depth of 9’-0”” in this context?
For those who do utility pad-mount work regularly:
Appreciate any insight from those familiar with utility primary installations.
Relevant details:
•Spec calls for (2) ¾” x 10’ copper-clad ground rods.
- Note states: “Install two 3/4” x 10’ copper weld ground rods driven to a minimum depth of 9’-0”.”
- There is a copper ground bus mounted in the transformer pad window (at finished grade elevation).
- The rods connect to that ground bus inside the window.
- Excavation is approximately 4’ deep below finished grade.
- Pad/window elevation is at finished grade.
- Primary and secondary conduits are already installed and and stubbed up from the excavation.
If I drive the rod from the bottom of the 4’ excavation:
- Driving 9’ would leave 1’ exposed at the ditch bottom.
- That would put the rod top 3’ below the pad window.
- I would not be able to reach the ground bus.
So it seems the only way to both:
- Achieve ≥9’ embedment, and
- Have the rod top land at the pad window for connection
Is to backfill/bring the area up to near grade and then drive the 10’ rod from that elevation.
Is that the correct interpretation of “driven to a minimum depth of 9’-0”” in this context?
For those who do utility pad-mount work regularly:
- Do you typically drive rods from finished grade elevation once the pad base is built up?
- Or is there another accepted method in this scenario?
- I’m concerned if I backfill then drive rods I run the risk of hitting the installed underground conduits. Primary side is robroy sweeps. Secondary side are pvs 90s.
Appreciate any insight from those familiar with utility primary installations.