AOGrady139
Member
- Location
- St Albans, Vermont, USA
Background for the question:
We ran a 400 Amp 3 Phase 120/208V parallel feeder from an already installed 400A MDP breaker. MDP was properly bonded to all required electrodes (building steel, rods, and concrete). The feeders ran to a panel in a retail space for a strip mall. We had an inspection by our state inspector for the energizing of this service and he informed us that the grounding conductor had to be sized per 250.66 Grounding Electrode Conductors. In the past we have always used 250.122 EGC's for this as it is only needed to supply return path for tripping of the OCPD. We sized each equipment ground conductor in the parallel runs at 1 AWG as it states for 400A OCPD under aluminum. Anyone have any idea as to where he is coming up with it? He is telling me it needs to be a 1/0 per 250.66.
We ran a 400 Amp 3 Phase 120/208V parallel feeder from an already installed 400A MDP breaker. MDP was properly bonded to all required electrodes (building steel, rods, and concrete). The feeders ran to a panel in a retail space for a strip mall. We had an inspection by our state inspector for the energizing of this service and he informed us that the grounding conductor had to be sized per 250.66 Grounding Electrode Conductors. In the past we have always used 250.122 EGC's for this as it is only needed to supply return path for tripping of the OCPD. We sized each equipment ground conductor in the parallel runs at 1 AWG as it states for 400A OCPD under aluminum. Anyone have any idea as to where he is coming up with it? He is telling me it needs to be a 1/0 per 250.66.