Hi,
As per the NEC table Table 310.15(B)(16), a 500 AWG conductor rated has an ampacity of 430 @ 90 degrees C. However, most motors and ALL circuit breakers as far as my limited knowledge are not rated to properly operate at 90 degrees C.
However, most of the conductors we use are based on 90 degrees C ampacities.
My question if most of the equipment aren't rated for this high temperature why have it in the first place?
As per Schneider Electric website "https://www.se.com/uk/en/faqs/FA290363/" it states that 90 degrees cables are not permitted on NSX MCCB.
As per the NEC table Table 310.15(B)(16), a 500 AWG conductor rated has an ampacity of 430 @ 90 degrees C. However, most motors and ALL circuit breakers as far as my limited knowledge are not rated to properly operate at 90 degrees C.
However, most of the conductors we use are based on 90 degrees C ampacities.
My question if most of the equipment aren't rated for this high temperature why have it in the first place?
As per Schneider Electric website "https://www.se.com/uk/en/faqs/FA290363/" it states that 90 degrees cables are not permitted on NSX MCCB.