Hello All:
I am designing a retrofit for distribution system and am currently selecting the cable sizes for the schedule.
I do not have a code question but would like your input as electricians/engineers.
What size of cables do you generally start specifying parallel runs?
Context:
-I have a need for a cable run with a rating of 250A
-My options are
1) 3 Phase + Neutral of 250 kcmil (75°C) in a conduit (255A rated)
2) 2 Parallel runs of 1 AWG (75°C) for each 3 Phase + Neutral in two conduits (260A rated)
What is the wire size cutoff that you find too hard to pull 4 conductors in commercial situations?
Cheers!