kwired
Electron manager
- NE Nebraska
- EC
So I googled why do we drive ground rods and I come across an electrical company in Maryland that claims its so that unwanted current travels to the ground to protect us from getting shocked in the event current is on a metal object ..equipment pipes etc.
This helps to confuse the whole purpose.
If bonding is the effective ground fault path for safety. Then the ground must be to bond the earth. Just kidding.
That is essentially the purpose of a grounding electrode. No guarantees you will get a low resistance path through earth though, and the reason earth paths are not allowed by NEC to serve in place of equipment grounding conductors or bonding jumpers.