Where do neutral and Equipment grounding conductor

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached exhibit shows neutral going to each service disco. In each service disco their is bar in which neutral lands.
Questions:

1. Is the bar in picture two separate bars bonded together or one bar?

2. In attachment Can neutral conductor connect in the same bar as equipment grounding conductor or additional separate equipment grounding conductor bar needs to be provided?
 

Attachments

  • 87EB8912-82F9-49B3-BCF0-A4286E84116E.jpeg
    87EB8912-82F9-49B3-BCF0-A4286E84116E.jpeg
    424.6 KB · Views: 22
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Each of those are Service Disconnects so the EG may be attached or landed on the respective neutral bar. A separate EG bar may also be installed, attached directly to the can per instructions. Additional neutral conductors may land only on the original neutral bar. EGs may land on either.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Each of those are Service Disconnects so the EG may be attached or landed on the respective neutral bar. A separate EG bar may also be installed, attached directly to the can per instructions. Additional neutral conductors may land only on the original neutral bar. EGs may land on either.

I am going to have install in which in each respective service disco the neutral conductor is going to land on the same bar as equipment grounding conductor, isolated grounding conductor land on the same bar. Bar inside each service disco shown post #1.

Don’t follow when you say EG
Maybe landed on the respective neutral bar? Are there cases it cannot be done?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
As Tom said, you're still in service equipment, so there is no separate equipment grounding system yet. The premises EGC system only begins when you leave the service equipment.

Everything attaches to the neutral itself. Even if you had a redundant EGC bar, installed the grounding electrodes are supposed to land on the neutral bus, not a separate grounding bus.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
The incoming service conductors go into the trough.

Mounted outside bonded with #6 AWG to the trough enclosure install also has intersystem bonding terminal. Can intersystem bonding terminal be bonded to the trough enclosure?
 