Service Conductors. The conductors from the service point to the service disconnecting means.
The service entrance conductors end at the service disconnecting means.
Here is the NEC definition from Article 100.
Chris
thanks... i'm just wondering why this electrician is trying to pull such big wires all the way to the panel...
Really? not in all instances.The Main Feeder conductors would have to be at least as large as the service entrance condutors.
Roger
Really? not in all instances.
This is a duplex , The feeder would be that of table 310 .15 B
The correct size if copper is # 2 CU
You must have that old Fart eye problem like I have.I really need to read more closely, I completely passed over the reference to the duplex. You know, it is Monday. (I picked up on that too when I went back and re-read the OP)
Roger
You must have that old Fart eye problem like I have.![]()
:grin:btw-
i DO have to read those definitions more often...
05 NEC...
o-k , so if he uses 310.15(b)(6), then he can run other wires in the same raceway? (if de-rated?) because it is a feeder , not Service entrance..