Where is pool bond wire ?

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Look around the pump motor or timer, or any other equipment for the pool. You probably won't see it in the panel as its not required to be there.
 

spark master

Senior Member
Location
cyberspace
ok,, it's running up the back of a 4x4 post which supports the pool panel.... and goes directly into the pool panel.
The aged copper actually blends in pretty nicely with the pressure treated post, which is covered in vegetation.
But anyway, goes directly into the pool panel, and I don't see split bolts or anything to make taps for the pump ground & heater ground....
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That one is likely not part of the pool bond grid (more likely a panel grounding electrode).
As suggested above. Look at the pump.
 

jusme123

Senior Member
Location
NY
Occupation
JW
xb4c3b282cc654ffcce965c40519f7502.png.pagespeed.ic.VIptWDAd3y.png

No equipotential bonding of panel shown, because it’s not required
 