- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
Existing (old, small) building. Only one panel: 175 amp, 120/208V, 3 phase, circa 1976. Served by outdoor pad-mounted, 112.5 KVA transformer. There is no conductor connected to X3. Hand-written label on panel says 120/208V-1 ph. There are 1-pole breakers in all 42 positions. Panel schedule shows most of them in use, including all three phases.
My best guess is that there is a jumper conductor between two of the phases, so that power can be fed to any breaker on any leg. I don’t know service conductor sizes, so I can’t say whether one leg is carrying too much current. My project will be adding load for HVAC equipment.
I want to tell the owner that the panel has to be replaced. I want to include code citations to forestall any gripes about cost. Other than 110.3B, what can I cite?
My best guess is that there is a jumper conductor between two of the phases, so that power can be fed to any breaker on any leg. I don’t know service conductor sizes, so I can’t say whether one leg is carrying too much current. My project will be adding load for HVAC equipment.
I want to tell the owner that the panel has to be replaced. I want to include code citations to forestall any gripes about cost. Other than 110.3B, what can I cite?