ramsy
NoFixNoPay Electric
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
I can't say for sure, but I don't think any of them are.
Curt Sqartz said:Crouse Hinds distribution equipment was renamed back to Murray when Siemens acquired the line. Murray breakers with the same part number can be used in Crouse Hinds equipment. Crouse Hinds equipment was named Murray before it was Crouse Hinds.
Cutler-Hammer acquired the Westinghouse distribution line which included Challenger. A Cutler-Hammer BR circuit breaker is the replacement for Westinghouse (Bryant) BR circuit breakers and Challenger C breakers. If you look at a BR breaker you will notice that it has both the Westinghouse and Challenger part numbers on it.
None of those breakers are automatically listed as being interchangeable with other manufactures. An Eaton BR is only listed for use with panels that accept type BR or type C breakers.
Eaton does make some Classified (CL) breakers for use with other manufactures load centers. The breaker instruction will include a list of exactly which load center it is classified for use with. A BR breaker is not a Classified breaker
Classified breakers contradict UL's own requirements. UL states that we must follow the instructions included with the equipment. The instructions with Square D load center state we must only use Square D breakers so to me that throws out the whole legitimacy of using classified breakers.
There are a few AHJ around me that will not accept classified equipment. Circuit breakers and recessed light trims are 2 items they closely watch.
...All are fine.
{image clipped}
For those who can't read the letter in this image "Murray Electrical Products, a brand of Siemens Energy and Automation, would like to advise all of its customers that the use on non-Murray labeled circuit breakers in a Murray load center will void the load center warranty..."
And regardless of warranty, they used the words "improper use."
I'll give that all due consideration, of course.
Interesting, because when I worked for Siemens, I had a similar letter to give out that stated that Murray and Siemens breakers were one and the same, totally interchangeable with each other. Of course, we were the dog, they were the tail...
Agreed, but that has usually nothing to do with whether or not they are legal... :lol:
True- but considering how they are one in the same now (Sylvania, Crouse Hinds, Murray, Bryant, BR, Eaton, ect) Id wager its a safe bet.![]()
Did the same OEM make both Murray and Bryant?
See Top & Bottom breakers in image bellow:
White Breaker, handle color, & label style seem identical with different markings.
Is the Top breaker (Murray EP 15-15) and bottom breaker (Bryant BRD 20-20) from the same MFG, or are these counterfeit equipment?
View attachment 18985
![]()
For those who can't read the letter in this image "Murray Electrical Products, a brand of Siemens Energy and Automation, would like to advise all of its customers that the use on non-Murray labeled circuit breakers in a Murray load center will void the load center warranty..."
I am tempted to say none. All are fine.
Honestly I don't remember the whole synopsis, but at one point I am mostly certain they did.