ptonsparky
Tom
- Occupation
- EC - retired
I have two 1hp 480v gear motors located within 20 feet of each other performing the same function and identically wired. Motor A failed an insulation test after 20 plus years. Replacement was Code C vs B, output speed is higher but FLA is lower. Three amp magnetic only breaker ahead of starter A would not hold on start of new motor. I temped motor A to motor B starter and all works fine. Ordered replacement reconditioned CB because new of same mfg is no longer available. Still won?t work. Moved CB of motor B to A. Works great. Neither old or new CB will now start Motor B. Both motor circuits were megged and starters checked. Both motors are now running with a borrowed CB and motor B actually has the higher inrush current of the two. (Fluke Power Quality meter)
I now have three 3 amp breakers that worry me. Are the two that now will not start either motor working correctly? Or the one that starts both the problem?