Which method would you select ?? and why??
Dwelling has 200 amp SquareD homeline panel with open slots.
Heater has (3) 240v 40amp elements (50amp max breaker)
Water hear closet is 40 ft away.
Method A
...... IN the main panel install (3) 50 amp breakers and run (3) 8/2 romex to individual 60amp pull-out disconnects.........then to the unit.
Method B
... Install 125 breaker in main panel to 1/0-1/0-2 Al SE cable to a 125 amp Main-lug subpanel located In the heater closet, then, use (3) 50 amp 2-pole breakers , then(6) #8 to feed the unit
Thank you for your input
Dennis
Dwelling has 200 amp SquareD homeline panel with open slots.
Heater has (3) 240v 40amp elements (50amp max breaker)
Water hear closet is 40 ft away.
Method A
...... IN the main panel install (3) 50 amp breakers and run (3) 8/2 romex to individual 60amp pull-out disconnects.........then to the unit.
Method B
... Install 125 breaker in main panel to 1/0-1/0-2 Al SE cable to a 125 amp Main-lug subpanel located In the heater closet, then, use (3) 50 amp 2-pole breakers , then(6) #8 to feed the unit
Thank you for your input
Dennis