Don't have my book handy but you can't have heater loads above 60A. They have to be divided.
This is from memory so the 60 may be wrong but do know you have to split up heavy heater loads.
I know there is wording like you mentioned, mostly applies to electric space heating from recollection. Might still be some instances where it doesn't apply.
Sometimes you run into a unit with a large supply circuit but still gets subdivided within appliance to circuits of 60 amps or less.
Not sure if this applies here but this is what I was thinking of...
(F) Electric Heating Appliances Employing Resistance-
Type Heating Elements Rated More Than 48 Amperes.
(1) Electric Heating Appliances. Electric heating appliances
employing resistance-type heating elements rated
more than 48 amperes, other than household appliances
with surface heating elements covered by 422.11(B), and
commercial-type heating appliances covered by 422.11(D),
shall have the heating elements subdivided. Each subdivided
load shall not exceed 48 amperes and shall be protected
at not more than 60 amperes.
It was 60A but the load can't be more than 48A because of the continuous load.
48 x 125% = 60