- Windsor, CO NEC: 2023
- Hospital Master Electrician
Question: I have been taught that when calculating the service for a structure served with 3?, you must take the nominal voltage and multiply it by the square root of 3.
For example, a calculated load of 450,000 VA in a 277/480 3? system, would look like this:
450,000 / (480 x 1.73) = 541 amps
In light of the other thread, it seems to me that the magic mysteries of 3? would only take place for genuine 3? loads. Line-to-neutral, or two-pole line-to-line loads shouldn't benefit from the "x 1.73" voltage correction, should they?
A load calc for a 3? system should be an addition of single-phase loads and three-phase loads, calculated separately, it seems to me.
But I'm probably missing something.
[ September 24, 2005, 11:14 PM: Message edited by: georgestolz ]