thanks how did you learn so much
Just to show Rob has no only learned so much, but he also has ESP, I will give you a "contrary opinion" :grin:
Actually I agree with him in general but add that, although there is no DIRECT Code requirement to do so, I have on a few occasions come across a Jucuzzi brand hydrotub which had manufacturer installation instructions which called for a #8 bond back to the panel.
Under those circumstances, many inspectors would require the bond per NEC 110.3(B).
I have attached a copy of the page that requires the bonds.
For that reason, I suggest you review the manufacturer instructions.
View attachment 4374
I have on a few occasions come across a Jucuzzi brand hydrotub which had manufacturer installation instructions which called for a #8 bond back to the panel.
.
View attachment 4374
Just to show Rob has no only learned so much, but he also has ESP, I will give you a "contrary opinion" :grin:
Actually I agree with him in general but add that, although there is no DIRECT Code requirement to do so, I have on a few occasions come across a Jucuzzi brand hydrotub which had manufacturer installation instructions which called for a #8 bond back to the panel.
Under those circumstances, many inspectors would require the bond per NEC 110.3(B).
I have attached a copy of the page that requires the bonds.
For that reason, I suggest you review the manufacturer instructions.
View attachment 4374
***** just don't read the mfg instructions.![]()
Dennis you are kidding ? Correct?
I ''''''try''''' to use common sense but I never ignore what is in the code or in the mfg. specs.
I was kidding but I personally, in this case,will never run that #8 back to the panel unless forced into it. No way- waste of money and ,IMO, it is the mfg. trying to cover their butts and have no idea what they are talking about.
I was kidding but I personally, in this case,will never run that #8 back to the panel unless forced into it. No way- waste of money and ,IMO, it is the mfg. trying to cover their butts and have no idea what they are talking about.
Dennis you are kidding ? Correct?
I ''''''try''''' to use common sense but I never ignore what is in the code or in the mfg. specs.
Never?Seriously NEVER?
I'm with Dennis on this one.