thanks how did you learn so much
Just to show Rob has no only learned so much, but he also has ESP, I will give you a "contrary opinion" :grin:
Actually I agree with him in general but add that, although there is no DIRECT Code requirement to do so, I have on a few occasions come across a Jucuzzi brand hydrotub which had manufacturer installation instructions which called for a #8 bond back to the panel.
Under those circumstances, many inspectors would require the bond per NEC 110.3(B).
I have attached a copy of the page that requires the bonds.
For that reason, I suggest you review the manufacturer instructions.
***** just don't read the mfg instructions.![]()
Dennis you are kidding ? Correct?
I ''''''try''''' to use common sense but I never ignore what is in the code or in the mfg. specs.
I was kidding but I personally, in this case,will never run that #8 back to the panel unless forced into it. No way- waste of money and ,IMO, it is the mfg. trying to cover their butts and have no idea what they are talking about.
Never?Seriously NEVER?
I'm with Dennis on this one.