Jim W in Tampa said:Thats ok cause i dont use romex.But i do question its use on mc.
Just shooting from the hip, I don't think that romex staples are OK for MC cable.
steve
Jim W in Tampa said:Thats ok cause i dont use romex.But i do question its use on mc.
hillbilly said:Just shooting from the hip, I don't think that romex staples are OK for MC cable.
steve
braiansore said:Are romex staples Listed for use with MC ? I don't think so. How about 110.3(B)? Try some Bridgeport Mc Clips instead.
iwire said:Edit, For that matter NM supports do not need to be listed either.
Jim W in Tampa said:Shooting from mine i cant cite a code number to say they aint legal.
iwire said:MC supports are not required to be listed.
You can support MC with a bent nail if you want.
Edit, For that matter NM supports do not need to be listed either.
allenwayne said:100% correct I until now never looked at 330.30 and all it says is secured,nothing about approved or listed means.I guess I wasted alot of energy carrying around MC straps ,screws and a cordless.
But 334.30 isn`t so liberal.it does list staples as a means of securing and it also says designed for that purpose.So everyone keep the NM staples and don`t use a bent nail on that romex
dlhoule said:Are you saying a properly bent nail supporting the MC is not designed for the purpose?
braiansore said:As long as it is listed no problem.
iwire said:Brian as far as the actual use of cable ties many of do that.
However if you have more than two MCs cable tied up a stud you will very likely have a violation of 300.4(D) which requires a 1.25" set back.
When that happens you need a product like the CJ-6.
How can it be a bundle when they are parallel? That inspector will be easily over ruled. Whatever... space your CJ's 25" apart or more, and the so-called "bundling" ruling goes out the window.jkoso said:I saw an inspector in St. Louis County fail an inspection for having four pieces of MC in Jim.
He said it was considered bundeling.
Anyone else have any experience with this?