Where did I go wrong in this conversation ??? Why can't a HO manage his own loads (not the ones connected to the ATS load shedding module) by shutting off the breakers. What have I said that was wrong ?
Because homeowners are not always home when power goes out, and like I said before if you have a generator that will automatically start, and a ATS that will automatically transfer, then the generator will be loaded with the full load of the house, the homeowner will have all the loads on if on normal power right?, do you think the homeowner can react fast enough when power goes out to get to the panel and turn off the loads that will over load the generator? what if the panel is in the basement and the homeowner is upstairs in his bedroom, thats two flights of stairs, or what if the home owner is out in the back yard working and doesn't even notice that the power went out.
Many of these newer generators start and transfer within just a few seconds, but it doesn't really matter, if you have more load connected to the generator that it can handle, it will burn up the alternator, sure some of the more expensive manufactures do have electronic overload detection built into their transfer switch, but your not going to sell that kind of generator to back up his power.
I don't know how to make it any plainer, then this, if the system is automatic it will automatically transfer the whole load that the homeowner would have on when running on utility, which in many cases is everything, if the generator is not sized for this amount of load it will be damaged, again the breaker on the generator is only sized for fault current, it is not there to prevent you from over loading the generator, that job is left up to us when we size the generator for the total demand load that the generator could see when the ATS transfers the load to the generator, this demand load is not like how we figure the size of a service for a house although you can use this method but most likely you will end up with a much larger generator than needed as the NEC builds in quit a bit of head room for safety, but you want to size a generator for the maximum demand load that the generator will see, yes it takes doing some homework but if you want to correctly install generators then its part of the job, I have seen a few try to use the utility bill to size a generator, no you can't do that either as that is an average of a months usage, but the demand load can far exceed that amount, also you must take into account of all motor loads that may try to start back up all at the same time, while motors when running on the utility will have a diversity factor as it would be very unlikely that more then just a few will try to start up at one time as they cycle to there own independent controls, but in the event of a power failure they can all try to start which can bring a generator to its knees, I get away with this by installing delay timers with different times so that no two motors will start up when the generator restores power, always set the largest motor to fire up first then the next size down and so on, this is because the larger running motors can act as a flywheel to help the other motors start.
I did a house that had a 5 ton A/C unit and a 3 ton A/C unit, the homeowner had already bought the 15kw generator and automatic transfer panel on EBay, well if it wasn't a good costumer and friend I would have walked, but using delay timers and current relays I was able to run almost his whole house on that generator, its been in operation for over 10 years without a problem the only loads we could not run was the built in double oven which was as old as the house and had mechanical controls that would allow it to come back on after a power outage, a hot tub and pool equipment, so we left these loads in the main service panel, I used the current relays between two freezers and two refrigerators so that if one was already on the current would keep a contact open and not let the other one start up until the first one finished its cycle, then the second one would run again its current would then keep the first one from running until it cycled off, but would these be a code compliant method of load shedding? I don't know, but the wiring was safe and it was installed in a code compliant manner and it kept the total demand load from exceeding the rating of the generator which was the main goal.
Just remember with a manual transfer switch a homeowner has time to select the loads he want or can run, with an automatic transfer switch he doesn't have the time to get the loads turned off and this can lead to damaging the generator which in most cases the manufacture will not repair under warranty look at any of the warranty disclaimers and most all will not cover the generator if it has been overloaded, so you could end up paying that bill to get it fixed, even with a manual TS if you do not spell out what loads the home owner can run and put it in writing and have him sign it so you have something to fall back on when the homeowner tries to push the generator a little more and don't think they won't they will but maybe not if they know if they damage the generator from over loading it then its their baby.
The story I posted earlier about the homeowner who thought he could get away with adding on his own the A/C unit to the ATS panel found out very fast that I would not be footing the bill, as I quickly showed him the paperwork he signed that included the instructions that installing any more loads to that ATS sub panel would result in a damaged generator and would void my warranty as well as the manufactures, so yes they will try to push the envelope if they think they can get away with it, it was a buddy of his who was an industrial electrician who happen to be at his house one the time when the electric went out on a hot day, that told him I was nuts that it would be no problem to add the A/C to the panel, well his buddy's miss information cost him quite a bit of money, I had even marked the panel with the words "do not add any loads to this panel or damage to the generator could result" which I also kept a photo of in the file on that house which is one reason I don't like doing manual transfer kits on a main panels that allow a homeowner to select which breakers they can turn on, because it requires allot more paper work and instruction to document that they know what loads they can run and what loads they can't.