This was kind of a toss up between putting this here and in the NEC forum. Kind of randomly I chose here as my part in this is more as an EC.
Looked at a job today where the HO had a generator installed. It is a 15KW w/ ATS. He bought it at Depot and had their recommended electricians wire it. Where to start?
~125' of 1" FMC w/ about 3/4 of outside (ie wet location). (15) 90 degree bends w/ no pull point. (3) #6 (H-H-N) and (1) #8 (G) plus 4 #14 (control). N and G were black the whole way. Breaker in the generator was a 70A. Generator feeds the main panel which is 200A rated. These are the highlights.
I told the HO that I would right up a proposal to fix this and site the code violations as I think there is clear recourse against the installing EC. W/O citing the articles (I'm feeling kind of lazy and don't feel like breaking the book out at the moment) I have 1) Too many 90's; 2) FMC in a wet location; 3) N and G not continuously marked; 4) Conductors undersized for the breaker size. I haven't calculated conduit fill yet but it "looks" OK.
Here is my question. It seems obvious to me that a 15KW generator protected at 70A is too small to run a 200A service. But the more I thought about it it seems that the only way to truly determine that is do a house calculation and see what the calculated load is. I guess we could probable also look at history from the POCO but I don't think that would count as one guy living alone is going to draw a whole lot less than if a family moves in there. It seems that this is a case where theory wins over reality.
So am I missing something or is a trip to article 220 the only way to show that this is a questionable installation?
Looked at a job today where the HO had a generator installed. It is a 15KW w/ ATS. He bought it at Depot and had their recommended electricians wire it. Where to start?
~125' of 1" FMC w/ about 3/4 of outside (ie wet location). (15) 90 degree bends w/ no pull point. (3) #6 (H-H-N) and (1) #8 (G) plus 4 #14 (control). N and G were black the whole way. Breaker in the generator was a 70A. Generator feeds the main panel which is 200A rated. These are the highlights.
I told the HO that I would right up a proposal to fix this and site the code violations as I think there is clear recourse against the installing EC. W/O citing the articles (I'm feeling kind of lazy and don't feel like breaking the book out at the moment) I have 1) Too many 90's; 2) FMC in a wet location; 3) N and G not continuously marked; 4) Conductors undersized for the breaker size. I haven't calculated conduit fill yet but it "looks" OK.
Here is my question. It seems obvious to me that a 15KW generator protected at 70A is too small to run a 200A service. But the more I thought about it it seems that the only way to truly determine that is do a house calculation and see what the calculated load is. I guess we could probable also look at history from the POCO but I don't think that would count as one guy living alone is going to draw a whole lot less than if a family moves in there. It seems that this is a case where theory wins over reality.
So am I missing something or is a trip to article 220 the only way to show that this is a questionable installation?