I recently installed several LED hi bays, replacing old 400 watt MH luminaires. One of them was really dim after turning them on. Went to check it out, factory apparently tied the dimmer leads together instead of leaving them capped like all the others were. I would presume shorting those leads togethergave it the "0" end of the 0-10 v input range and it was dimmed as much as it can be dimmed. Took that connection apart and capped both leads and it was as bright as the other luminaires.
shorting the purple and gray together is the quick and dirty test for your dimmable lights
if you don't have a lighting panel or dimming controls in place. as all i do any more is drive
around and watch lights not work correctly it seems, before i go off to do a certification, i
get the electrician who wired the occupancy on the phone and ASK if he's tested the lights
this way...
me: have you actually TESTED the lights?
sparky: everything is wired good.
me: what does that mean?
sparky: they are all on.
me: have you tried dimming them?
sparky:
me:
sparky: how do you do that?
me: short the purple and gray wires together. do they dim? go try it now, while we are on the phone.
sparky: some of them do. the other lights must be broken.
me: the lights are most likely ok. the wiring is open, missing, or reversed. it's gotta work before the lights can be certified.
sparky:
me:
sparky: the lights are in a hard ceiling. what do i do now?
me: suicide is an option. have you considered it yet?