Ground readings
Ground readings
We read ground rods very often due to the fact that we are installing systems under a state written(actually it's all copy and paste work by an overpaid consulting group )spec.Here is the grounding section.
NOTE: Grounding shall meet the minimum requirements of the NEC.
NOTE: Grounding shall meet the minimum requirements of the NEC.
Provide permanent and continuous grounding circuits with a current-carrying capacity high enough and an impedance low enough to limit the potential above the ground to a safe level.
Perform grounding as follows:
1. Bond the grounding circuits to nonferrous metal driven electrodes. Use electrodes that are at least 0.625 inches (15 mm) in diameter, 8 feet (2.4 m) long, and are driven straight into the ground.
2. Use the shortest possible ground lead that leads directly to a grounding source.
3. Ensure that the maximum resistance between the ground electrode and the cabinet ground buss or other point in the grounding system is no greater than twenty five (25) ohms.
4. Connect the ground electrodes and the ground wire with an exothermic weld.
5. Connect neutral conductors to the cabinet buss-bar and ground them at each terminal point.
6. Ground the cabinet with a No. 6 AWG solid copper wire between the buss-bar to the ground electrode. Bends shall not exceed 4 inch (100 mm) radius bends.
7. Permanently ground the poles by bonding the No. 6 AWG solid copper wire to a separate ground rod.
8. Ground pole-mounted accessories to the pole.
9. Underground metallic conduit or down guys are not acceptable ground electrodes. Do not use Snap-On connections.
10. For extended distances between Ramp Meter and IVDS additional grounding may be required by the manufacturer.
Alot of times have been told that we had to get 25 ohms or less( it used to be 5!!!)We have tried multiple rods only to find the readings going up and with sectionals the same thing at times 10'-38.63/20'-40.78/30'-40.58/37'-41.2 and no further penetration. We only use clamp on type meters for one reason how can you do a 3 point in the middle of the concrete jungle.
Ground readings
We read ground rods very often due to the fact that we are installing systems under a state written(actually it's all copy and paste work by an overpaid consulting group )spec.Here is the grounding section.
NOTE: Grounding shall meet the minimum requirements of the NEC.
NOTE: Grounding shall meet the minimum requirements of the NEC.
Provide permanent and continuous grounding circuits with a current-carrying capacity high enough and an impedance low enough to limit the potential above the ground to a safe level.
Perform grounding as follows:
1. Bond the grounding circuits to nonferrous metal driven electrodes. Use electrodes that are at least 0.625 inches (15 mm) in diameter, 8 feet (2.4 m) long, and are driven straight into the ground.
2. Use the shortest possible ground lead that leads directly to a grounding source.
3. Ensure that the maximum resistance between the ground electrode and the cabinet ground buss or other point in the grounding system is no greater than twenty five (25) ohms.
4. Connect the ground electrodes and the ground wire with an exothermic weld.
5. Connect neutral conductors to the cabinet buss-bar and ground them at each terminal point.
6. Ground the cabinet with a No. 6 AWG solid copper wire between the buss-bar to the ground electrode. Bends shall not exceed 4 inch (100 mm) radius bends.
7. Permanently ground the poles by bonding the No. 6 AWG solid copper wire to a separate ground rod.
8. Ground pole-mounted accessories to the pole.
9. Underground metallic conduit or down guys are not acceptable ground electrodes. Do not use Snap-On connections.
10. For extended distances between Ramp Meter and IVDS additional grounding may be required by the manufacturer.
Alot of times have been told that we had to get 25 ohms or less( it used to be 5!!!)We have tried multiple rods only to find the readings going up and with sectionals the same thing at times 10'-38.63/20'-40.78/30'-40.58/37'-41.2 and no further penetration. We only use clamp on type meters for one reason how can you do a 3 point in the middle of the concrete jungle.