680.23(B)(2)(b) Wet-Niche luminaires ,"Where a nonmetallic conduit is used, an #8 AWG copper EGC shall be installed in this conduit unless a listed low-voltage lighting system is used . The EGC shall be terminated in the forming shell, J-box or XFMR enclosure." Its my understanding that if you have a nonmetallic conduit you would run a #8 EGC from the forming shell to the J-box that is set 4' from the pool to supply power to the pool lights. At the J-box if you have a 120V circuit with a #12 EGC supplying power to the light why then the need for the #8 EGC if all you have going back to the panel is a #12 EGC? Does it have something to do with corrosion? Thanks.