Smart $ raises a point:
"Don't forget that the grounded conductor is bonded to the GES. That in itself helps 'stabilize' the system voltage, which is the point of bonding the GES. The downside is, yes, there can be voltage gradients across the system... but ask yourself, what is the alternative? Do you think fewer electrodes will change the voltage gradients imposed on conductors from a nearby lightning strike?"
There's a lightning expert with a PhD on this site, and if he speaks up I will fall silent.
In the meantime, if I've understood what I've read, multiple grounding locations means opening the door to ground loops. "Fewer electrodes" makes things worse, but designing with fewer points of attachment to the GES reduces the chance of damage. Ideally there should be only one point.
To put in another way, if you don't feed step potential into the conductors by grounding them at distant points, then you don't have the "voltage gradients imposed on conductors from a nearby lightning strike".
"What is the alternative?" Smart $ is asking a great question here. There's a terrible downside to a system-wide shared grounding point in the main structure, the kind of system I've seen advocated. Imagine lightning striking the detached building. Running that current inside the main building on its way to ground invites disaster.
"Don't forget that the grounded conductor is bonded to the GES. That in itself helps 'stabilize' the system voltage, which is the point of bonding the GES. The downside is, yes, there can be voltage gradients across the system... but ask yourself, what is the alternative? Do you think fewer electrodes will change the voltage gradients imposed on conductors from a nearby lightning strike?"
There's a lightning expert with a PhD on this site, and if he speaks up I will fall silent.
In the meantime, if I've understood what I've read, multiple grounding locations means opening the door to ground loops. "Fewer electrodes" makes things worse, but designing with fewer points of attachment to the GES reduces the chance of damage. Ideally there should be only one point.
To put in another way, if you don't feed step potential into the conductors by grounding them at distant points, then you don't have the "voltage gradients imposed on conductors from a nearby lightning strike".
"What is the alternative?" Smart $ is asking a great question here. There's a terrible downside to a system-wide shared grounding point in the main structure, the kind of system I've seen advocated. Imagine lightning striking the detached building. Running that current inside the main building on its way to ground invites disaster.