The title says everything, you know so yeah. Why do certain wiring devices have the ratings 125v, 250v.
What I was told by a Hubbell rep regarding this a long time ago:There are nominal supply voltages and there are equipment ratings.
Isn't that what I said?. . . it was bumped to 120/240V and made a national standard.
. . . they settled on 125/250V as a design standard . . .
Didn't sound the same.Isn't that what I said?![]()
Want more confusion - motors and appliances often marked 115 or 230.The title says everything, you know so yeah. Why do certain wiring devices have the ratings 125v, 250v.
Want more confusion - motors and appliances often marked 115 or 230.
For 480 volt nominal the motors are usually marked 460 volts, supply volts often is close to 500 (no load anyway) but devices are marked 480 or sometimes devices marked 600 volts are used or is only thing available that will work for the application.
What I was told by a Hubbell rep regarding this a long time ago:
For a time in the early days of electrification, most residential distribution voltage standards were 110/220V. In the late 20s, design standards for equipment mfrs, like NEMA, came into being. Then in the 30s with the REA (a Depression era government program to provide electricity to farms and rural areas) it was bumped to 120/240V and made a national standard. So NEMA, having to now adjust their design standards to match, anticipated the distribution voltage standard possibly increasing again and they settled on 125/250V as a design standard so that they would not have to change again for a long time.
125 volt to neutral wye system still not so even at about 216.5 line to line.I wish we had gone to 250 volts. Nice, even, round number.
125 volt to neutral wye system still not so even at about 216.5 line to line.
The title says everything, you know so yeah. Why do certain wiring devices have the ratings 125v, 250v.
Yes, I was just elaborating on your response because it was an otherwise useless chunk of information rattling around in my brain...Isn't that what I said?![]()
What about 460? I haven't seen 440 on a motor since ones made in the 1930s....At 480 all we have is 480 and 440.
“200-250” is a very weird voltage class. In three phase equipment distribution can be 240 delta, 208 wye, or even 220 V under European
standards with similar single phase equipment. Equipment for these voltages tends to be wide range.
What about 460? I haven't seen 440 on a motor since ones made in the 1930s....