CajunTech
Member
- Location
- Watson, LA, USA
I have commissioned several sites on east coast that a single panel generated an isc value (usually 8 amps) which would allow a single panel to cause failure of the gfdi fuse (per utility scale allowing 5 amp fuses). Now having commissioned sites on the west coast they use panels of 1.5 amps isc with the same 5 amp gfdi fuse. This would mean there could be many square yards of charged area of possible metal racking and wire combination creating a uninterrupted current sourced circuit till other circuits also fail then adding to the fault current till enough combined current can open the fuse. I have looked for code compliance's that would mandate a coordination of the gfdi fuse be rated for the isc of a single string but can not find such code.