Hello, I have a scenario where I am scratching my head as to why the original designer went through all of the complexity to require a Zig Zag transformer. Maybe some one here can give me a different perspective to some of the advantages that could have been the reason to do it in such a way. The following is the system setup:
There is a concrete pier in the middle of a river. This pier has many motor loads and some lighting loads. The pier is fed from one side of the river from one utility grid and from the other side of the river from another utility grid (redundant services, only one feeding at a time, switched between the two by an ATS at the pier). Both utility services are 208/120V but are stepped up to 480VAC 3W 3Phase. 3 phase conductors are sent to the pier, no neutral, no ground through a submarine cable (from each utility). The services terminate at an ATS on the pier which is considered the pier service entrance. At the ATS there is a connection to a grounding transformer (the zig zag transformer) where a ground is established. On the pier there is a separate 480V Delta to 208/120 Transformer for lighting loads. At the zig zag transformer a ground fault relay is installed to monitor the 3 phases to the zig zag. Each of the utility services are low, at the 208/120 service level, each are only 250A (again only one service feeding at a time).
Question: Why didn't the designer just send a neutral and a ground from each utility which is on shore? Then have the neutral be switched at the ATS if there was any concern of the two utilities being connected at all?
There is a concrete pier in the middle of a river. This pier has many motor loads and some lighting loads. The pier is fed from one side of the river from one utility grid and from the other side of the river from another utility grid (redundant services, only one feeding at a time, switched between the two by an ATS at the pier). Both utility services are 208/120V but are stepped up to 480VAC 3W 3Phase. 3 phase conductors are sent to the pier, no neutral, no ground through a submarine cable (from each utility). The services terminate at an ATS on the pier which is considered the pier service entrance. At the ATS there is a connection to a grounding transformer (the zig zag transformer) where a ground is established. On the pier there is a separate 480V Delta to 208/120 Transformer for lighting loads. At the zig zag transformer a ground fault relay is installed to monitor the 3 phases to the zig zag. Each of the utility services are low, at the 208/120 service level, each are only 250A (again only one service feeding at a time).
Question: Why didn't the designer just send a neutral and a ground from each utility which is on shore? Then have the neutral be switched at the ATS if there was any concern of the two utilities being connected at all?