This would have been if they instituted a regular wye secondary. I missed that it was a delta and no connection to the utility since it is a SDS. Seems like the designer choose very specifically to have the step up transformer be a 208V Delta to 480V delta. So that no SDS grounding of neutral was required since no neutral exists.
Just because you have no neutral doesn't relieve you from grounding something else, or providing an ungrounded system with ground fault detection. And if you have ungrounded system it still doesn't relieve you from providing EGC's and bonding all non current carrying items like you normally do, that is what makes the link between services on each side, and even though you don't have any neutral current from the facility served, doesn't mean there isn't a path through your grounding network for utility neutral current to flow.
And by design isolates all of the on premise grounding from any PoCo grounding.
Yes, but you still need an EGC and ultimately that will tie both utilities together via main bonding jumpers on the service equipment.
I doubt it. Sounds to me like the utility feeds premises wiring then voltage gets transformed from premises wiring to pier.
EGC's still required and introduce a solid path between the two services grounded conductors.
There is a neutral on the 208Y/120-V service derived system; but we are saying there is no neutral on the 480-V separately derived system.
As I mentioned above, does not relieve grounding the secondary or using GF detection, and you still need GES and EGC's tied to non current carrying components.
Assuming things are done properly, non current carrying metal parts of an electrical system, even if its an SDS with the secondary ungrounded, Will be connected to the utility MGN (if the utility supply is an MGN). So the EGc's and/or metal parts at the pier will provide a low impedance path for the MGN. That is the theory anyway. OP said there wasnt an EGC so maybe they deliberately skipped it to break the path for the MGN, although seems like the cable armor might be bridging the two systems.