There is nothing in the NEC that can be used to support that calculation method.
What says we can't use it???
There is nothing in the NEC that can be used to support that calculation method.
What says we can't use it???
What says we can't just make up our own way?
Right i used 4/0 instead of #4Actually 4-250kcmil and 1- #4 is 1.4414 IN2 so that means I'm under by .1084. :grin:
But if the NEC does not prohibit it then we can. So again, what's say we can't?
110.3(B) .......... the LB is listed and it has a clear label, unless we are told otherwise IMO we are stuck with it.
110.3(B) .......... the LB is listed and it has a clear label, unless we are told otherwise IMO we are stuck with it.
That IMHO is code compliant unless you can prove it's not.
Price the LB, price a 6?6?36 wireway and my time to make two KO's. Now price your time dealing with the inspector. I have the same problem here and until we can all get on the same page, the Kennedy method for 4 wire installs.
I don't know the article the inspector quoted yet. But just got word he failed me for having a 3" PVC LB with (4) 250 MCM AL and (1) #4 AL in the LB. From what I heard he's saying you can't have more than 3 wires in an LB!! Max fill on this 3" LB says this: MAX 3-350MCM , 178 CU IN. How am I over this? And how can he say you can only ever have 3 wires in an LB?This is starting to become a HUGE issue in a nearby city we work in. I am trying to figure out this madness because the way they are inspecting LB's and failing because of them, you might as well never use one ever again! Bottom line is if you have more then 3 wires then you are wrong according to this city, which I want to fight because then every LB existing in this world is wrong then. Need some insight please.
6 sets of paralell 650 kcmil's
6 sets of paralell 650 kcmil's
650 kcmil's ?
Maybe im reading it wrong but wouldn't 314.28(C) allow the use of smaller LB's that have combinations of conductors.
(3) Smaller Dimensions.
Boxes or conduit bodies of dimensions less than those required in 314.28(A)(1) and (A)(2) (6 times or 8 times) shall be permitted for installations of combinations of conductors ......(that are less than the maximum conduit or tubing fill (of conduits or tubing being used) permitted by Table 1 of Chapter 9,)53,31,40% ........ provided the box or conduit body has been listed for, and is permanently marked with, the maximum number and maximum size of conductors permitted.
Meaning that the 3" lb that is smaller that the 6 X rule can be used, and shall be permitted for installations of combinations of conductors can be used??:?
Price the LB, price a 6?6?36 wireway and my time to make two KO's. Now price your time dealing with the inspector. I have the same problem here and until we can all get on the same page, the Kennedy method for 4 wire installs.
![]()
Copper or aluminum?How many #4's can you get in a piece of 3/4" ?