wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
An AFCI breaker has a microprocessor to track current vs time to identify arc signatures and trip. Given that, why does it still have a conventional thermal trip element? The microprocessor could do the same time averaging of current that the thermal element physically does, and implement the trip curve electronically. The trip curve would not be dependent on ambient temperature like the behavior of a thermal element is. (Unless the electronic current measurement method is temperature dependent, not sure how that happens internally).
And then, given that the electronics could implement any trip curve desired, it should be a simple matter to make every AFCI breaker a 100% rated breaker. My understanding of the 125% factor for continuous currents is that it is a reflection of a mismatch between the time vs current shape of the trip curve of a thermal element, and the time vs current shape of installed conductor damage curves (or some other limit on allowable short duration overloads). Namely that when the thermal element is tuned to provide the desired behavior at short time periods, it ends up overly sensitive for long time periods, and may trip at long durations for current under the breaker's rating. But if the trip curve is implemented electronically, it can be reshaped to no longer have this mismatch between short and long durations.
So am I missing something here?
Cheers, Wayne
And then, given that the electronics could implement any trip curve desired, it should be a simple matter to make every AFCI breaker a 100% rated breaker. My understanding of the 125% factor for continuous currents is that it is a reflection of a mismatch between the time vs current shape of the trip curve of a thermal element, and the time vs current shape of installed conductor damage curves (or some other limit on allowable short duration overloads). Namely that when the thermal element is tuned to provide the desired behavior at short time periods, it ends up overly sensitive for long time periods, and may trip at long durations for current under the breaker's rating. But if the trip curve is implemented electronically, it can be reshaped to no longer have this mismatch between short and long durations.
So am I missing something here?
Cheers, Wayne