See 230.43 for the wiring methods that are permitted for service conductors. There are cable wiring methods permitted in that code section.
Sometimes the power company has specifications that limit the wiring methods, and sometimes there are local amendments to the NEC that limit the wiring methods, but in most cases the selection of the service entrance wiring method is a design choice by the designer using one of the wiring methods listed in 230.43.
However the rule in 300.5(C) limits the use of cable wiring methods under a building. If I have to run a raceway under the building because of this requirement there is no reason to use a cable wiring method. Individual conductors are a better choice where a raceway is installed.