To get an accurate OD measurement, use 2 squares.
which is against code.
I'm correcting someone else's mistake.
Inside that 4" duct there's an electrical line .
The electrical line is running through a communications box, which is against code.
My plan is to carefully cut the 4" PVC duct (without damaging the conductors inside)
and take a 8" x 8" x 4" Nema 4R box and put a box adapter on it as shown on the right.
Then we flip it upside down and put it on top of that 4" duct and reroute the electrical ine
to a new Panel/Disconnect and TVSS. I can't find a box adapter that will slip inside the PVC or outside it.
What code?
is it a trick of the image, or is that white, not grey? Because I'm wondering if someone used drain pipe...
The gray straight-edge on the left does not look quite perpendicular to the square; it will hit the marks on the two edges of the square equally when it is.
QUOTE]
+1 the squares are not square, check the other leg of the blue square, should read the same. Even on the pic, one edge of the blue is closer to 4-9/16, the other 4-5/8 = NOT square.
as the bard saith, much ado about nothing.
I thought it was "sayeth".as the bard saith, much ado about nothing.
]National Electrical Safety Code (NESC), Section 320 B 2, Separation From Other Underground Installation. It states, "Separations Between Supply and Communication Conduit Systems: Conduit systems to be occupied by communication conductors shall be separated from conduit systems to be used for supply systems by 75 mm (3 in.) of concrete, 100 mm (4 in.) of masonry, or 300 mm (12 in.) of well-tamped earth."
]When telecommunications cables are routed nextto large electromagnetic fields, surplus voltage andcurrent can be induced on them. If the power levelof the electrical cable is large enough, the electricalnoise can interfere with operation and performance ofthe telecommunications applications running on thecabling. Electrical and data systems designers must befamiliar with this phenomenon and ensure that the twosystems can work in harmony.
I thought it was "hisself".You are correct, the bard 'hiself' always used the -eth form
]National Electrical Safety Code (NESC), Section 320 B 2, Separation From Other Underground Installation. It states, "Separations Between Supply and Communication Conduit Systems: Conduit systems to be occupied by communication conductors shall be separated from conduit systems to be used for supply systems by 75 mm (3 in.) of concrete, 100 mm (4 in.) of masonry, or 300 mm (12 in.) of well-tamped earth."
]When telecommunications cables are routed nextto large electromagnetic fields, surplus voltage andcurrent can be induced on them. If the power levelof the electrical cable is large enough, the electricalnoise can interfere with operation and performance ofthe telecommunications applications running on thecabling. Electrical and data systems designers must befamiliar with this phenomenon and ensure that the twosystems can work in harmony.