iwire said:
dnem said:
I don't find that genuine reputable electricians screw up multis on common breakers. But I do find good electricians far too often follow a trained pattern of landing the black and red side by side. It's a pattern that works great for regular breakers but can be a disaster on minis.
One of the biggest potential dangers from electrical fire is the overloaded neutral. With no OC it sits there and burns.
David in a home panel with both legs of a MWBC on the same leg as you describe what is the actual chance of a neutral 'burning'?
Look at the 310.16 rating of 12 and 14 AWG.
Not that I am saying it is a good thing when a MWBC is landed improperly just that I do not think it is the disaster you make it sound like. :wink:
I opened a panel one time and wondered why they used brown wires for neutrals. When I examined more closely, they were white neutrals that had turned brown, dry, and cracked insulation. The insulation just flaked off to the touch. Since that time I've seen a number of panels with brown flaky neutrals.
Using the simplist example, on a house single split phase system. If you have a properly installed multi: When the black 12gauge phase wire is loaded to its maximum of 20amps and the red 12gauge phase wire is loaded to its maximum of 20amps, the neutral will have no current flow since there's no unbalanced current.
But if you
don't have a properly installed multi and the black and red get landed on the same side of the single split phase: Then when the black 12gauge phase wire is loaded to its maximum of 20amps and the red 12gauge phase wire is loaded to its maximum of 20amps, the neutral will have
40amps of current flow. Table310.16 gives 30amps for 12gauge THHN, but since 240.4(D) cuts back the OC, I doubt there is a much of a fudge factor built in.
If the breakers are tolerating more than 20amps, which happens more often than many people imagine, you can get
over 40 on the neutral. Now add higher ambient inside the panel and you have insulation that is getting hotter than it can handle without damage.
How many of you guys have seen brown crusty neutrals in a panel ?
David