This is the manual btw but I cant get it to load on here ![Frown :( :(](data:image/gif;base64,R0lGODlhAQABAIAAAAAAAP///yH5BAEAAAAALAAAAAABAAEAAAIBRAA7)
I'm also with you on this. I think it was even more common years ago then it has been more recently to see same motor and same 120 volt control timer used on 120 volt gas dryer as was used on the 120/240 volt electric dryer made by same manufacturer.I disagree, dryers have always needed a neutral. In fact the NEMA 10-30r receptacle has always been classified as none grounding 3 pole 3 wire.
Also, its not just the controls:
I'm also with you on this. I think it was even more common years ago then it has been more recently to see same motor and same 120 volt control timer used on 120 volt gas dryer as was used on the 120/240 volt electric dryer made by same manufacturer.
How much do you want to bet that when that dryer eventually fails and gets replaced by a 120/240 dryer the person who installs it will just wire your cord to the new dryer as if it were two hots and a neutral? And it would not qualify for the exception, of course, even if that person moves the panel end from ground bar to neutral bar.Don't know I had that one that the nameplate was 240v. only two terminals only green wires. or green with yellow. I did not look at the schematic though.
I used a 240v and ground cord and cap. not a dryer type.
How much do you want to bet that when that dryer eventually fails and gets replaced by a 120/240 dryer the person who installs it will just wire your cord to the new dryer as if it were two hots and a neutral? And it would not qualify for the exception, of course, even if that person moves the panel end from ground bar to neutral bar.
![]()
I once had to install range receptacles in an apartment complex that originally had gas ranges, as well as install cords and set the ranges in place as I changed them. These were only 24 inch wide ranges (apartments were small and range space was limited otherwise typical 30 inch range likely costs less just because they produce more of them).Don't know I had that one that the nameplate was 240v. only two terminals only green wires. or green with yellow. I did not look at the schematic though.
I used a 240v and ground cord and cap. not a dryer type.
I disagree, dryers have always needed a neutral. In fact the NEMA 10-30r receptacle has always been classified as none grounding 3 pole 3 wire.
Also, its not just the controls:
When you say that dryers have "always" needed a neutral just how far are you going back? "Always" can be quite a long time.
The appliance repairman that told me that older dryers didn't need a neutral did so in 1981 and he had been in the appliance business since the late 40s or early 50s.
The automatic clothes dryer for residential use went on the market just before world war two and I have never seen a wiring diagram for one of the older one's.
There is no real good reason for a dryer to need a neutral even today. The British will sell you one that doesn't.
There are millions of older homes out there that have not been rewired and in most cases it would have been cheaper all around to have a 240V dryer and use the third uninsulated conductor as ground.
The idea of bonding the frame of a dryer to neutral was a very bad idea (think open neutral).
Don't know I had that one that the nameplate was 240v. only two terminals only green wires. or green with yellow. I did not look at the schematic though.
I used a 240v and ground cord and cap. not a dryer type.
How much do you want to bet that when that dryer eventually fails and gets replaced by a 120/240 dryer the person who installs it will just wire your cord to the new dryer as if it were two hots and a neutral? And it would not qualify for the exception, of course, even if that person moves the panel end from ground bar to neutral bar.
![]()
When you say that dryers have "always" needed a neutral just how far are you going back? "Always" can be quite a long time.
The appliance repairman that told me that older dryers didn't need a neutral did so in 1981 and he had been in the appliance business since the late 40s or early 50s.
The automatic clothes dryer for residential use went on the market just before world war two and I have never seen a wiring diagram for one of the older one's.
There is no real good reason for a dryer to need a neutral even today. The British will sell you one that doesn't.
There are millions of older homes out there that have not been rewired and in most cases it would have been cheaper all around to have a 240V dryer and use the third uninsulated conductor as ground.
The idea of bonding the frame of a dryer to neutral was a very bad idea (think open neutral).
There is no real good reason for a dryer to need a neutral even today. The British will sell you one that doesn't.
It is just a matter of unit cost. They save every cent they can on each unit.
I have worked on homes with very old dryer receptacles and wiring. They have all been NEMA 10-30's. I don't think I have ever run across a NEMA 6-30 dryer receptacle.
I have a Wiring simplified book that goes by the latest code, which was 1962 when the book was printed.
I like to see their explanations that lead to some of the older wiring I have seen or worked on.
For clothes dryers it reads:
Dryers are 230 volt devices although some have 115 volt motors in them. The Code requires that the frame of the dryer be grounded. But permits it to be grounded by means of the neutral conductor in the wiring, { provided it is #10 or larger} so 3 wire cable must be used even if the entire dryer operates at 230 volts. The code considers dryers to be portable devices.
Well, even back then the 1962 code said it needs to be a 3 wire cable. The change in 2014 NEC, seems to be from the neutral to the equipment ground. As the neutral is being utilized with the device. With an Exception: For existing branch circuit-installations only where an equipment grounding conductor is not present in the outlet or junction box the frames of clothers dryers shall be permitted to be connected to the grounded circuit conductor. But it has to be at least 10 AWG.
As far as the early 50s and Im sure it was earlier. Even vintage models have 120 volt motors. The appliance tech may not have known the difference between ground and neutral for a dryer.
I agree, not to mention so many DIYs (and even sparks back then) screw it up. Around here tons of condos have 10-2 going to the dryer with the bare EGC landed on the ground bar. Even my uncle who was an electrician taught me dryers only need "2 hots and a ground"
The manufacturers could just have easily used a 240V motor for the gas dryer because with only the motor load it would not have needed to be larger than #12 or even #14 and the only difference would have been the breaker and receptacle. Today you wouldn't need arc fault or GFCI.
There is no real good reason for a dryer to need a neutral even today. The British will sell you one that doesn't.
It is just a matter of unit cost. They save every cent they can on each unit.
True, but consider not all homes had 240 back then. In fact some manufactures let you re-wire their 120/240 electric dryers to 120 volt having 1/4 the heating power. It was even listed on the nameplate.
In reality straight 240 volts would have been best, but back then things were different which set the trend we see today.
I hadn't thought of that. I grew up living in the country and most all of the services were 240V because of the electric ranges ( no gas available ). People tended to get electric ranges years before electric dryers so as to stop chopping wood and overheating the house in summer. . Those automatic dryers were expensive and not a necessity, clothes lines were cheap and the sun worked for free.