As I was always told...."It is what it is."
Isn't that Charlies' Rule?
As I was always told...."It is what it is."
Isn't that Charlies' Rule?
The ampacity of 12 gage THHN is 30 amps, per 310.16, but
240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied.
(3) 14 AWG Copper. 15 amperes
(5) 12 AWG Copper. 20 amperes
(7) 10 AWG Copper. 30 amperes
Most electricans then state the ampacity of 12 AWG THHN is 20 amperes, when its actually 30.
This provision has been in the NEC for a long time, its only for 14,12 and 10 AWG, 18 and 16 were added in the 2008 NEC.
Why does the NEC restrict the overcurrent protection on these small conductors?
So some of the Idiots out there in the field dont kill everyone????.
So some of the Idiots out there in the field dont kill everyone????.
Isn't that the purpose of the entire NEC?
I think the OPs question is why are three specific wire gauges limited to what's referred to as the small-conductor rule. Why aren't all the others treated the same way?
By telling him that's not what you want.(How often do you get a complete and honest answer from an engineer?)
maybe because , 20 amp breakers are nicer looking than 30 amp breakers?
And they call me strange! :roll:maybe because , 20 amp breakers are nicer looking than 30 amp breakers?
maybe because , 20 amp breakers are nicer looking than 30 amp breakers?
Too bad I can't remember any of it.Cool collection Ken. Whats realy impressive though is the fact that you can tell us the history of all this. Wow!
The ampacity of 12 gage THHN is 30 amps, per 310.16, but
240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied.
(3) 14 AWG Copper. 15 amperes
(5) 12 AWG Copper. 20 amperes
(7) 10 AWG Copper. 30 amperes
Most electricans then state the ampacity of 12 AWG THHN is 20 amperes, when its actually 30.
This provision has been in the NEC for a long time, its only for 14,12 and 10 AWG, 18 and 16 were added in the 2008 NEC.
Why does the NEC restrict the overcurrent protection on these small conductors?