Why no 125A 3 pole breakers?

Status
Not open for further replies.

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It's about the potential energy in the circuit.

So if you look closely, you will see that the 2P 125A breakers are only listed as "slash" type, meaning 120/240V. That means that in the event of a asymmetric fault (line to ground), the fault energy seen by the circuit breaker is potentially never more than what will flow at 120V (line to ground). But in a 3 phase 240V delta system, even at the same amount of fault current the asymmetrical fault energy can be 240V to ground, so twice the potential fault energy . That's why you must use "straight" 240V rated 2 or 3 pole breakers in a 240V 3 phase panel and you can only use 1 pole slash rated breakers in a "High Leg" system on the 2 phases that are referenced to ground.

3 pole breakers would never be able to be used in a single phase panel, so they ALL have to be "straight" rated for 240V. When used in a 3 phase panels then, the worst case potential fault energy of an asymmetirical fault on a 3 pole breaker would be 2 phases to ground, so that would be twice the energy potential of a 2 pole 125A slash rated breaker.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
So the question is, why can't they make a slash rated 3 pole breaker? Why can't say Eaton give their customers a $14 buck 3 pole?
 
It's about the potential energy in the circuit.

So if you look closely, you will see that the 2P 125A breakers are only listed as "slash" type, meaning 120/240V. That means that in the event of a asymmetric fault (line to ground), the fault energy seen by the circuit breaker is potentially never more than what will flow at 120V (line to ground). But in a 3 phase 240V delta system, even at the same amount of fault current the asymmetrical fault energy can be 240V to ground, so twice the potential fault energy . That's why you must use "straight" 240V rated 2 or 3 pole breakers in a 240V 3 phase panel and you can only use 1 pole slash rated breakers in a "High Leg" system on the 2 phases that are referenced to ground.

3 pole breakers would never be able to be used in a single phase panel, so they ALL have to be "straight" rated for 240V. When used in a 3 phase panels then, the worst case potential fault energy of an asymmetirical fault on a 3 pole breaker would be 2 phases to ground, so that would be twice the energy potential of a 2 pole 125A slash rated breaker.

I did propose this as a possibility in post #12 😇
 