electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
I know that GEC stands for "Grounding Electrode Conductor": it is the conductor from the service panel to the grounding electrode. The point I was making in my post is that a GEC is a conductor for grounding (electrically connecting to the grounding electrode). Whereas an EGC is for BONDING electrical equipment to the breaker panel: it provides a safety fault path for tripping the OCPD; it is not used for grounding to earth.
I will first say that I am on the side of the fence that says we should change it to "EBC" and get "ground" out of it. However, note that the part of your post that I Bolded, is not correct. The NEC DOES require us to connect equipment to earth - it says so right in the beginning of article 250. Granted it is of relatively minor importance compared to bonding to the source for fault clearing, but nonetheless we are also required to connect to dirt so what you said is not really accurate. Technically then, it should be called an "equipment grounded and bonding conductor."