Had an interesting situation on an installation.
The State of TN requires NRTL certification on equipment.
On a recent install the facility has a SCA of 45k not counting motor contribution.
A new piece of equipment for controlling (30) 25 hp motors was installed. The control cabinet did not meet the requirements of 409.110 ('08). In complying, the manufacturer supplied a nameplate indicating a SCCR rating of 65k.
To meet the State requirement, they had a UL field evaluation performed and as a result the new, UL certified nameplate shows a withstand raring of 5k.
Obvioulsy a potential danger that would have remained unchecked were it not for the NRTL requirement.