Can someone please give me a scenario where a standard 120/240v double pole breaker will fail or be overloaded If used on a 240v corner ground delta service? I know it’s not code and you’re supposed to use straight 240v breakers because phase to ground is 240v in a delta and not 120v. But the only difference I can see is that the plastic housing of the breaker itself being in contact with the metal cover of the panel has a higher voltage potential phase to ground in a corner ground than in a 120/240v single phase service. Am I really supposed to believe that the plastic that the 120/240v is made out of can’t handle the higher voltage potential between the phases and the panel cover but CAN handle the ever present 240v phase to phase voltage potential within the breaker itself? I call BS!