Probably because over that distance, there is not enough fault current to trip the breaker in its instantaneous range. But that is just a WAG.
There was a proposal a few cycles ago that would have required testing to prove the system could source enough fault current at the end of the line receptacle to open the OCPD in its instantaneous range, but it was rejected.
Perhaps enforcement? If this were passed what would be an easy way of verifying? Dummy load testing? Each point on a circuit would be different? Cant ohm it out, too impractical?There was a proposal a few cycles ago that would have required testing to prove the system could source enough fault current at the end of the line receptacle to open the OCPD in its instantaneous range, but it was rejected.
Perhaps enforcement? If this were passed what would be an easy way of verifying? Dummy load testing? Each point on a circuit would be different? Cant ohm it out, too impractical?
That's how you do it on paper. That's not reality. You do a job, and the inspector show up and says,Chapter 9 Table 9
Loop impedance testing ?I just bought a tester that determines available fault current at the point it is connected, don’t know how accurate it is, but I was surprised at how low the available fault current was at my house. Haven’t used it yet in a commercial setting.
I just bought a tester that determines available fault current at the point it is connected, don’t know how accurate it is, but I was surprised at how low the available fault current was at my house. Haven’t used it yet in a commercial setting.
Not a job for a megger, which measures high resistance values at high voltages. Instead you need a device to measure low resistances, often a four terminal measurement.Aside from a full megger.
Can't the results of a voltage drop tester such as the Ideal SureTest be worked mathematically to give an available fault current at that point on the circuit? That device provides the following voltage drop testing.
% Voltage drop under load (12A, 15A, 20A load tests): 0.1% - 50.0%