How do you define an effective ground fault current path though? If you mean direct contact, sure. Yet thats not ULs or the CMP's reasoning behind GFP and GFCIs in many locations.
I would define it two ways. First is resistance needs to be low enough to trip the ground fault protection in the event of a fault with a grounded metal surface. Obviously this is a moving target. We can always make ground fault detection more sensitive especially if in doing so we increase the minimum trip time. The GEMI approach actually looks at effective grounding from the phase overcurrent perspective. With ground fault detection and tripping obviously much lower limits are acceptable. The GEMI approach applies to a basic thermal magnetic breaker on say a 300 foot conduit run.
Second is to restrict transients to some reasonable maximum such as 1.0 per unit. So this implies draining the system capacitance. In high resistance grounds we want to set the resistor to no larger than 300% of the system capacitance Xc or it acts like an ungrounded system with the attendant transient issues. This is a very reasonable maximum for effective grounding. NEC requires solidly grounded systems under 250 V but that certainly doesn’t restrict “effectively grounded” at long distances from the transformer.
Again don’t forget that “effectively grounded” in terms of Earth grounding is a short distance issue. Earth resistance is inversely proportional to distance so that “remote Earth”, say a mile away or so, is under 1 ohm and certainly better than any intentional conductor. Edison was right if you get far enough apart and “stray voltage” is acceptable.