Example…
200amp upgrade with new meter and panel ourside
Original fuse box inside became sub fed
3 wire sub panel with seu
In a dwelling
Grounds and neutrals tied together
If the bare neutral conductor was lost, what would happen? Wouldn’t the load try to balance between the 2 phases? And then the rest of the current would try to flow onto any metal that’s bonded and energize it and become a shock hazard?
Wouldn’t the same shock hazard be if the service neutral was lost? (Lost service neutral is much more likely than lost sub panel bare neutral conductor). At the first MOD ground rods should also be bonded (but it’s a very high resistance parallel path) and possibly water line or gas line bonded.
Trying to understand why it’s so important we don’t 3wire sub panels (with bonded grounds and neutrals).